Mass Transfer - Engineering
Q1: In a forced draft cooling tower, water is cooled from 95 to 80°F by exposure to air with a wet bulb temperature of 70°F. In this case, theA range is 15°F.
B approach is 10°F.
C both (a) & (b).
D neither (a) nor (b).
ANS:C - both (a) & (b). Let's break down the concepts of range and approach in the context of a cooling tower and explain how they are calculated:
|